ddproduction Posted November 8, 2010 Share Posted November 8, 2010 Hi all, just a quick one: Does anyone know if DMX signals are likely to be affected across phases i.e. if the board and dimmers are on separate phases, will this cause any adverse effects? Thanks! :** laughs out loud **: Link to comment Share on other sites More sharing options...
TonyMitchell Posted November 8, 2010 Share Posted November 8, 2010 The DMX control protocol is electrically isolated, so no it will cause you no problems. Indeed it is common for larger dimmers to operate across multiple phases. Link to comment Share on other sites More sharing options...
Unfathomable Posted November 9, 2010 Share Posted November 9, 2010 I have always been advised to add a splitter with opto-isolation or similar to act as a buffer should anything try to fry your desk (better lose the >£100 splitter than the desk, right?). Nothing wrong with doing it though. Link to comment Share on other sites More sharing options...
csg Posted November 9, 2010 Share Posted November 9, 2010 DMX will operate correctly over different phases, with most touring dimmer racks being 3 phase, this would soon show up to be an issue if it were not the case. The important thing to maintain is the earthing of the system - DMX networks can get upset when connected between different electrical systems, earthed to different grounds. In this scenario, there is the potential for equipment damage in severe cases, and in all cases isolation should be used between the systems. Link to comment Share on other sites More sharing options...
ddproduction Posted November 9, 2010 Author Share Posted November 9, 2010 Thanks for all this - we are working in a village hall so earthing shouldn't be a problem :** laughs out loud **: Link to comment Share on other sites More sharing options...
d_korman Posted November 9, 2010 Share Posted November 9, 2010 Thanks for all this - we are working in a village hall so earthing shouldn't be a problem :** laughs out loud **: I've always found with Village Halls that earthing is the biggest problem - in fact I've got a show at one of these in two weeks time where we always have DMX issues, in spite of usein DMX distribution and terminators! Link to comment Share on other sites More sharing options...
Sound In Gloucestershire Posted November 9, 2010 Share Posted November 9, 2010 yeah village halls are always the worst in my personal experience, random pops and cracks and lights acting funny! Link to comment Share on other sites More sharing options...
timsabre Posted November 9, 2010 Share Posted November 9, 2010 Just going back to post #2 The DMX control protocol is electrically isolated, so no it will cause you no problems. This is incorrect (unless you have specifically fitted isolated DMX splitters). DMX is not electrically isolated. Csg is right that it's the earthing that will determine whether you have problems or not. Link to comment Share on other sites More sharing options...
Brian Posted November 9, 2010 Share Posted November 9, 2010 DMX receivers, if designed as per the recommendation of the spec, are isolated. Sadly, most manufacturers ignore this and simply implement the 'allowed' topology of non-isolated receivers, or worse, grounded receivers. Link to comment Share on other sites More sharing options...
timsabre Posted November 9, 2010 Share Posted November 9, 2010 DMX receivers, if designed as per the recommendation of the spec, are isolated. Sadly, most manufacturers ignore this and simply implement the 'allowed' topology of non-isolated receivers, or worse, grounded receivers. They don't ignore it, it's an engineering decision based on cost. I design this stuff for a living and a lot of the time the large additional cost of isolating the DMX cannot be justified in the cost of the product. Hence the vast majority of DMX equipment is not isolated, only the really expensive stuff is. Link to comment Share on other sites More sharing options...
Grum Posted November 9, 2010 Share Posted November 9, 2010 DMX receivers, if designed as per the recommendation of the spec, are isolated. Sadly, most manufacturers ignore this and simply implement the 'allowed' topology of non-isolated receivers, or worse, grounded receivers. They don't ignore it, it's an engineering decision based on cost. I design this stuff for a living and a lot of the time the large additional cost of isolating the DMX cannot be justified in the cost of the product. Hence the vast majority of DMX equipment is not isolated, only the really expensive stuff is. Or another way of putting it would be that your company chooses to ignore the specification in order to produce a product at a lower cost. Two sides of the same coin. Link to comment Share on other sites More sharing options...
ddproduction Posted November 9, 2010 Author Share Posted November 9, 2010 OK I see, the question I was tending to is will using DMX cross-phase cause any damage / adverse effects to the lights/dimmers/supply? :) Link to comment Share on other sites More sharing options...
Ynot Posted November 9, 2010 Share Posted November 9, 2010 OK I see, the question I was tending to is will using DMX cross-phase cause any damage / adverse effects to the lights/dimmers/supply? :)And the answer, as already quoted, is a firm 'no' - it will NOT be a problem.Isolation of the DMX stream from the desk itself is good practice, BUT is not essential. Link to comment Share on other sites More sharing options...
timsabre Posted November 10, 2010 Share Posted November 10, 2010 DMX receivers, if designed as per the recommendation of the spec, are isolated. Sadly, most manufacturers ignore this and simply implement the 'allowed' topology of non-isolated receivers, or worse, grounded receivers. They don't ignore it, it's an engineering decision based on cost. I design this stuff for a living and a lot of the time the large additional cost of isolating the DMX cannot be justified in the cost of the product. Hence the vast majority of DMX equipment is not isolated, only the really expensive stuff is. Or another way of putting it would be that your company chooses to ignore the specification in order to produce a product at a lower cost. Two sides of the same coin. No, this is not another way of putting it. Using the word "ignore" is an offence to all those engineers who labour hard in darkened rooms to bring you new DMX toys at a price you can afford. The specification either allows it or it doesn't and in this case, it does. Sorry to go off the topic. Link to comment Share on other sites More sharing options...
Recommended Posts
Archived
This topic is now archived and is closed to further replies.