Hi folks, we own 3 Desisti/Robert Juliat 5k fresnels which can be converted to HMI, and we're using two of them in the latter mode for our Christmas show. We're having something of a problem with the ballasts, in that they frequently trip the breaker for the 32a supply on striking up. The ballasts are Robert Juliat model A4/2500 and I gather that these units are pretty old. Is this a known issue at all (couldn't find anything with searches)? And if so, is there a fix, or a replacement ballast?

 

Thanks in advance,

 

GTG

Link to comment
Share on other sites

HMIs use more power that the lamp is rated for typ 4K = 21A running current at 230V Igniter pulse is not a lot so do not worry there. If the ballast is a cheapo and has no PFCs then add 50% to all currentsLikewise if the ballast is old and the PFCs have dried up then + 50% A rough test for old capacitors is clip on meter on the leads, they should show substantial current 5 to10A (this is subtracted at right angles from the total amps) There are usually several paralleled Cs so you can check with a clip on at various points on the chain and arithmetic which are working. Do be very careful inside a ballast, dangerous and expensive, also usual HMI warnings, full of hard UV turn of immediate if lens is damaged, strike voltage can be 70,000 volts. For magnetic ballasts there is also a + 50% current during the warm up phase, electronic ballasts should correct this.

 

So worst case for a 4K on 230v with a magnetic and no PFC A x PFC? x Start up => 21A x 1.5 x 1.5 = 47.5 A

Scale for other size HMIs

 

As the warm up is 2 mins then sequence starting will not help, a good clip on will help you understand what is flowing.

 

Link to comment
Share on other sites

Electronic ones often match more than one power so will run 2.5 / 4 kW or 1200W / 2.5 kW so have 2 different outlets

 

Electronic ones probably have LCD display / LEDs

 

Magnetics are incredibly heavy - indicators probably neon

 

 

Post a picture if you can

 

Do the MCBs trip at the moment of strike or after a short time?

 

Can you measure the running current on a good strike

 

If it is marginal an extra 20M of cable might reduce inrush,

Link to comment