Hi All

Help required!,

my minds thrown a blank, when using a truss on a pair of wind-up stands, how is the total weight loading calculated?

 

for example...

 

8m span of truss, supported on a pair of wind ups, each windup is capable of max loading of 180KG (assuming an evenly distributed load)

 

Thanks

Link to comment
Share on other sites

Look at the load figures for the truss your using. It will say what the UDL (as well as CPL, TPL, etc..) is @ 8m.. Or at least it should do!

 

That's the figure to go off, obviously if this is more than the capacity of the stands, or in fact the other way around, well.. you work to the lower rating.

 

T

Link to comment
Share on other sites

Don't forget the weight of the 8m of truss itself!

 

Not to mention the consequences of one of the stands being strapped to a speaker stack and tied in the middle to the false ceiling to stop it sagging, and someone 'dancing into' one of the speaker stacks.

Link to comment
Share on other sites

Don't forget the weight of the 8m of truss itself!
IIRC, most loading spec's include the weight of the spans themselves in the calc's for what UDL/CPL you can apply to the truss, so this isn't usually an issue.

 

I'm sure there's some that don't, so check on any paperwork to see if it mentions the spans own weight.. if not speak to the truss manufacturer!

 

T

Link to comment
Share on other sites

I would have thought that the weight of the truss was important when checking that the capacity of the windups is not exceeded.

 

The other thing to look out for is that if it is wound up unevenly there can be significantly more weight placed on one of the stands.

Link to comment
Share on other sites

Don't forget the weight of the 8m of truss itself!

 

Not to mention the consequences of one of the stands being strapped to a speaker stack and tied in the middle to the false ceiling to stop it sagging, and someone 'dancing into' one of the speaker stacks.

 

 

Don't forget the weight of the 8m of truss itself!
IIRC, most loading spec's include the weight of the spans themselves in the calc's for what UDL/CPL you can apply to the truss, so this isn't usually an issue.

 

I'm sure there's some that don't, so check on any paperwork to see if it mentions the spans own weight.. if not speak to the truss manufacturer!

 

T

 

I think j_b meant when calculating the loading of the wind up stands, in which case you do need to factor in the weight of the actual truss.

Link to comment
Share on other sites

Given that you are inside and on an even floor, you need to add up the weight of all your componants, and dveide evenly over the two stands. however you probebly need to offset the loading to one side to allow for the cable coming off on one end andallow for the weight of the cable drop.

 

If in doors make sure that the height of the structure is no more that three times the smallest dimension of the footprint of the stands. The more weight you add the more top heavy the overall structure can become. This can be rectified by adding weight to the bottom of the stands, which is probbly not a bad idea anyway.

Link to comment
Share on other sites

So, you wouldn't wind a typical manfrotto stand up then?

I don't think they make one, but perhaps you can enlighten me: which stand in Manfrotto's range has a max height greater than 3x the max width of its base?

 

Type 19, Type 40 etc.

Or from others Supertower's go 4:1, & if you're being anal a Doughty Zeniths over 3:1

Link to comment
Share on other sites

  • 3 weeks later...

If your using Prolyte truss get their product book and all the loading tables are in it!!!! start there me thinks

on a 9 meter lenth of H30v you can get around 199Kgs but an 8 meter span on 2 stands.........your looking at 80+Kgs for the truss before loading....