Emma Tooze Posted October 1, 2012 Share Posted October 1, 2012 Just wondering if I can run 2 36W fluorescents from one non-dim circuit? I think the circuits are 3Kw and they work through 15 amp so I'm assuming that should be fine? Link to comment Share on other sites More sharing options...
dbuckley Posted October 1, 2012 Share Posted October 1, 2012 If the non-dims are relay switched, then no problem at all. If the non-dims are semiconductor switched, there may be all sorts of problems. Two, 36W fittings may be a bit of an underload, and the leakage through the semiconductors (depending on the type of fluoro) may cause the fluoros to flicker dimly or flash intermittently; if so add a ghost load. If the fluoros are switch start (ie they flicker and flash at startup) there's a chance they could damage the switching element. Proceed with caution. Link to comment Share on other sites More sharing options...
ScottishCol Posted October 2, 2012 Share Posted October 2, 2012 Emma, can I make a suggestion? Does the fluorees have to dim? Run fluorees off a fixed mains switch. Mix with main theatre lights. Win? Col x Link to comment Share on other sites More sharing options...