Tempus 12 to new Demux unit Problems!!!


GaryCatlin

Recommended Posts

Hi all,

 

I am new here, and would like some help with a project I have been given. My school have placed me incharge of the school stage, this has an old Tempus 12 dimmer unit on it, now the lighting board that was with it is broken. I have got a demux unit to change the new DMX signal to analouge so the current tempus unit will work. Now the problem I have is wiring the 8 pin dim that comes out of the tempus unit into the 24pin on the back of the De-multiplexer unit I can not find a simple diagram to tell me on the net can anyone help please!!!

Link to comment
Share on other sites

Before we can help, you need to tell us which demux you have. The pinout of the the Tempus connectors can be found here.

 

The Tempus racks use the same configuration as the Zero88 connector. However they need 0 -> -10V control voltages and not the more common 0 -> +10V. I hope the demux you have is switchable.

Link to comment
Share on other sites

Before we can help, you need to tell us which demux you have. The pinout of the the Tempus connectors can be found here.

 

The Tempus racks use the same configuration as the Zero88 connector. However they need 0 -> -10V control voltages and not the more common 0 -> +10V. I hope the demux you have is switchable.

 

Yes the Demux is a BOTEX ME-72 MULTI EXCHANGER I found the tempus wiring on the net, but its the connections on the demux box I am having problems with, I have tried two different ways so far the first all light were flickering when the light desk was set to black out, I kinda figured that was wrong ;) the second attemp all the lights come up and fade down again but are on one fader on the lighting desk.

Link to comment
Share on other sites

Thanks Paul I have looked at the post, but could not find anything about wiring from the tempus box to the demux box.

 

It is in there if you look hard enough,

 

From Tom Baldwin's post dated 3 May 2004 12.47

 

i.e.

 

pin 1 chan 1

pin 14 chan 2

pin 2 chan 3

pin 15 chan 4

etc

with pin 13 ground.

 

Also there is a spec sheet linked from this topic - Botex ME-72

 

http://www.blue-room.org.uk/index.php?show...mp;#entry196276

Link to comment
Share on other sites

Thanks Paul I have looked at the post, but could not find anything about wiring from the tempus box to the demux box.

 

It is in there if you look hard enough, this may be better

 

http://www.blue-room.org.uk/index.php?show...mp;#entry196276

 

 

Thanks Paul again ;) been really helpfull. I shall give it ago see what happens, am I right in thinking that pin 13 is ground for both sets of dimmers?

Link to comment
Share on other sites

am I right in thinking that pin 13 is ground for both sets of dimmers?

 

Yes.

 

Make sure you've got the output set to -10v on the switches on the rear of the demux too. Strange things (and possibly smoke!) will happen if it's set wrong.

 

Just tried what Paul said about re-wiried the plug,and what adamharman said about pin 13, and away it went, great, thanks to all for you help. :) :(