Hi,

 

I have been asked by an old school which I used to attend, how they can change the sockets to 15amp.

 

They want to use a local theatre tech to do it, who said he can do it , but surely theres loads of rules and regs?

 

Can someone advise, best regards

 

alex

Link to comment
Share on other sites

If they are leaving the patch at 5A and the dimmers have 5A fuses per socket, then there's not an issue in safety, though I would like to see a warning sign up notifying of a 5A max per line in case anyone used a 15-5 (with a hired or new rack) and then overheated the wiring.

 

As above it is the retesting that is the issue.

Link to comment
Share on other sites

I have been asked by an old school which I used to attend, how they can change the sockets to 15amp.

 

They want to use a local theatre tech to do it, who said he can do it , but surely theres loads of rules and regs?

For a school situation there is only ONE course of action.

They need to get a theatrical electrical company in to carry out the work, and that company will HAVE to satisfy the local county council's regs and be approved. And they'll probably need 2 or 3 quotes. The county will likely have d0m3st1c sparks on contract, but in most theatre applications these guys will NOT have the necessary experience to do the job as it should do.

 

To quote an example I think I've mentioned here before: My wife teaches at a local primary school, and I get dragged along to supply and run the tech gear for their annual show. This year I said to the head that they really needed to get a new supply in for the lighting which would allow a safer feed and let me bring in a little more than before without risking over-loads. I specified a 32A minimum 3-ph setup on 3 x Ceeform sockets, even e-mailed a basic spec. I said that whilst not qualified to do the work in a school myself, I'd happily speak with their contracted sparky to settle any queries/details.

As usual, the install didn't go ahead til the week before the show and after I'd chased it with them... No-one had checked the spec with me, so I'd assumed they understood my detailed statements - what did I get? 3 nice 32A Ceeforms?

Nope - 3 twin 13A d0m3stic sockets on a single 32A rated ring main from their dis board!! I really should have known better !! :)

 

Back at the plot - by all means have a good idea of what YOU think the school should want, and give any tendering supplier the specifics, but they should be able to quote for what's actually needed.

Link to comment
Share on other sites

Would it not be more sensible to put a set of new IWB's in with 15A plugs so that WHEN (and there will be a time) the dimmers need replacing, the wiring is already suitable for the 15A load? Changing the patch bay as well would be sensible and relatively inexpensive I would have thought...

 

I do have to agree with everyone else though, the testing is the rules and regs. Often the charge for testing (by a trained and competant person) works out cheaper if that person was to do the whole job!

Link to comment
Share on other sites

You've said that the existing dimmers are already rated 15A

 

The existing IWBs have 5 amp sockets? So they probably don't have wiring that can handle 15A. So, unless you have 5A fusing in the dimmers you have a potential problem if a fault develops inside the IWB, whatever the socket on the end is.

 

In which case the suggestion to replace the bars is probably correct, unless you are prepared to strip out all the wiring and replace with the correct rating.

Link to comment
Share on other sites

You've said that the existing dimmers are already rated 15A
I wonder what sort of weird dimmers have been installed (Ah, re-read and they are Acts, but which?)? Most UK supplied dimmers have 15A sockets fused at 10A. On this assumption, it is unlikely that wiring would need to be changed. At the basic level 1mm single and T&E is good for 14A (various factors need to be applied, grouping, containment etc) and it is unlikely that anything as small as 1mm has been installed.

 

Someone competent needs to look at the system as a whole to decide what, if anything, needs upgrading along with a change to 15A plugs and sockets.

Link to comment
Share on other sites

Appologies I missed the fact that the dimmers were rated at 15A. So let me get this straight...there are 15A dimmers with a 5A patch bay and 5A sockets? Sounds quite unsafe to me unless the dimmers are fused at 5A per channel?
Link to comment
Share on other sites

For a school situation there is only ONE course of action.

They need to get a theatrical electrical company in to carry out the work, and that company will HAVE to satisfy the local county council's regs and be approved. And they'll probably need 2 or 3 quotes. The county will likely have d0m3st1c sparks on contract, but in most theatre applications these guys will NOT have the necessary experience to do the job as it should do.

If it is properly specified, the school's own/contract electrician should be fine, and probably somewhat cheaper. After all it seems like a case of changing plugs/sockets, possibly re-pulling cables, and retesting. As seen from other threads, employing 'threatrical electrical companies' doesn't obviate the need to specify the job properly, in writing, and get that to the right people.

Link to comment